Can I connect 3″ water heater vent to furnace vent pipe connector outside the chimney?

Home Maintenance Questions and AnswersCategory: Furnace VentingCan I connect 3″ water heater vent to furnace vent pipe connector outside the chimney?
Question by Scott

I just recently had to run new 4″ furnace pipe down through my old chimney because there was too much condensation forming inside of the chimney and getting into my house. My hot water heater is also ran into that chimney. My question is, can I connect my 3″ hot water heater line into my furnace pipe just outside of the chimney? The water heater requires a quarter of an inch in every foot and I can exceed that by an inch.

1 Answers
Best Answer
Dariusz Rudnicki Staff answered 1 year ago

Hi Scott,
If you have a 4″ furnace vent pipe / liner inside the chimney, it would be too small to support your WH and furnace venting. The basic requirement for two appliances venting into a common chimney is that the diameter of the chimney flue must be at least largest vent pipe + 50% of the smaller diameter. In your case this would be 5.5″ (6″ because they don’t make half sizes).
So, the proper way would be to have a 6″ diameter chimney flue instead of the installed 4″ and then both appliances connected to it – You can do it on the outside of the chimney, but the connector has to be 6” x 4” x 3” (“Y” if furnace has an induced draft motor) or “T” if both natural draft appliances. That 6” end would have to tie into the 6” liner. If you have a brick chimney with 4” hole, you’d have to make the opening larger to accommodate 6” diameter pipe… If it’s easier, run both pipes separately into the new 6” liner. You can use single wall if there are sufficient clearances to combustibles – at least 6”, and if the area pipe runs through is conditioned and fully accessible (not inside the walls, ceiling, etc.)
If your WH vents into that unlined chimney at this moment (next to the furnace pipe), this might also prevent proper drafting and cause more condensation and furnace pipe deterioration… especially during the cold season. Increasing WH vent pipe pitch will not help in this case…

Your Answer

5 + 11 =

Pin It on Pinterest

Share This

Share this post with your friends!

I'm selling my checkthishouse.com domain and this website.

I created it in 2001 for my home inspection business so it's a well established property with around 150 home improvement related posts. It also comes with a Youtube channel and a Q&A forum.

Website can be easily adopted for any home inspection / home improvement related business. Makes money on daily basis without even being touched, although it could make much more, I just don't have time to maintain it.

If you're an Illinois based home inspector I'll add http://homeinspectorillinois.com domain to this deal.

Inquiries and legitimate offers ONLY -

 Click HERE

BUY THIS WEBSITE!